• Why not take a moment to introduce yourself to our members?

DallasNYC

Advanced Reefer
Location
Manhattan
Rating - 100%
45   0   0
The circuit breaker in your electric panel will decide what you can load on it. Circuit breakers are rated in Amps, and they can vary. 15 amps is very common on outlet and lighting breakers. Watts = Volts * Amps. So the total amps you are using now is Amps = Watts/Volts. Or Amps = 1500w/115v = 13 amps. So if you have a 15 amp breaker, you are very close to the limit.
 

FRY

Senior Member
Rating - 100%
26   0   0
the safe load on any breaker is 80 % of the breaker rating, it is best to use 2 circuits on tanks half pumps on one circuit and the other on the second circuit,if one fails the other is still working half of the pumps,try to split up load between the 2 circuits you don't have to use full capacity
of the breaker to use 2 circuits
 
Last edited:

masterswimmer

Old School Reefer
Vendor
Location
NY
Rating - 99.6%
450   2   0
duke, In addition to Franks explanation of splitting everything up and to answer your question in another way, if you have one plug in that circuit and it's drawing 14 of your 15 amps, you don't have any room for any more plugs.

However, if you have 12 plugs in another circuit with each appliance drawing .5 amps, you'd still have more room for additional plugs/appliances on that circuit (9 amps additional, not subtracting the 80% rule Frank suggested).

So the # of plugs in a circuit is really incidental.

swimmer
 

Sponsor Reefs

We're a FREE website, and we exist because of hobbyists like YOU who help us run this community.

Click here to sponsor $10:


Top