I have a 92G corner reef.
Equipped with:
CPR overflow box with aqualift pump and filter for aqualift pump (LOUD AS ALL HELL)
Glass tops (small black plastic triangle is off)
Current nova extreme 4 bulb t5 156w with 2 daylights, 1 actinic and 1 purple + integrated fan (sits 1/2" off of glass)
Oddysea 18" metal halide 150w 10k with remote ballast (ballast is about 3 feet away from setup) with (2) 18w t5 actinics and integrated fan 186W TOTAL (raised on 3-4" legs)
Natural Wave wavemaker (3 outlets for powerheads) strapped to back of stand
(3) hydor koralia power heads 3,4 and 5 i think
Ecosystems refugium with 18w pc light (in stand)
CPR in-sump protein skimmer (rio 600)
Current Gamma 25w UV sterilizer (in stand)
Blueline 55 (90 watts) external pump (in stand) that goes to a 2 valve manifold
First valve goes to the main return which is full open to an Eheim spraybar about 24-30" long
Second valve is throttled down slightly as water passes thru the uv and chiller and then returns into a smaller Eheim spraybar with an elbow on the end without a cap as not to restrict flow I guess because it is too short maybe 8" in total
Current Prime 1/4 hp chiller which is next to the tank with control panel and display facing wall so condenser side blows into my living room without any restriction
4" RadioShack Server fan (I think) that blows a pretty serious amount of air. Enough that in the colder months I have to turn it off when I work under my tank 'cause it is too cool of a breeze. This fan is cut and mounted into the stand blowing into the stand.
....................................................................................................
My house is naturally warmer than most. I'm in a single family raised ranch with an attic above so it is more like I live on the second floor. My chiller was turning on 6-8 weeks ago and has gotten progressively worse as far as how often it runs. Back when we had 70 degree days or less it would turn on for 1-2 minutes and off for 10 minutes. Now with the warmer weather we were having last week it would be on for 1-2 minutes and off for 5 and back on again all day long. A few weeks ago the ambient temp in my house was 74-76 degrees. Now it is more like 80-84.
I started running my actinics at 6pm to 11 pm (so I can enjoy my tank after work) and my daylights run from 11PM all night until 7am where the actinics stay on for another hour. I started doing this to cut down on overheating the tank and to stop from draining my wallet over an electric bill with my chiller. NOTE: I have 3 setups so 3 chillers can be crazy to pay for. We really don't use ac unless we cant take it because we have lots of live plants in the house. Electric is cheaper in the off-peak hours.
36" Current light cooling fan exhausts thru the back ( I guess for closed canopy applications) and the MH is behind it as my tank gets narrower towards the back because it is a corner tank. Point being that the cooling fan from the 36" light blows through the beam of light from the 150w MH so you can hold your hand under the MH and it only feels slightly warmer but not hot.
When my hand is in the tank and I raise it to just below the surface i can feel a pretty dramatic temperature difference from the rest of the tank to water surface. This is why I removed the black triangle so heat can escape but I don't think it helped much.
I bought this setup second hand.
The only problems that I noticed which I will/have correct/corrected are:
1) the chiller was in the stand and eventho the fan was added it is still a heat source. Now it is on the side of the tank. Putting it in the basement isn't really an option because that is my Landlord's storage space.
2) The blueline 55 has a 1" outlet that goes into a check valve and before it goes into the 2 valve manifold it is already reduced to 1/2" and both outlets off of the manifold are 5/8 tubing. I have to upsize the 1/2 into the manifold I think because it is a big restriction to go from 1" down to 1/2" without the pressure having a place to go. My thinking is that the water may be slowed down a bit too much and is absorbing heat from my blueline pump. I hear that they are heat machines but if the water is slowed down too much then I imaging that it would just amplify the issue.
My tank gets minimal sunlight which is mostly indirect. When it really starts to get hot I will pull down the shades.
The small black triangle on the back of the glass canopy is off to help heat escape and so that my MH can brighten up the dark spot of my tank.
Tank has about 150#'s of live rock and about 50#'s of dead skeletal corals that I've cured to use as live rock and a ph buffer
.......................................................................................................
Simple math got me thinking:
blueline 55 is rated for upto 1100gph and upto 28 ft of head. If I was getting 1100 (which I know I'm not) and If i had 100 gallons between refugium and DT. It would take 6 minutes for the tank to go thru my Chiller but my chiller runs for less than 2 minutes and turns back on in 5 minutes. These past 2 rainy days it hasn't come on much at all so I know it isn't just stuck in some kinda crazy cycle. But I changed it's program. Before when it was turning on and off all day long it had a 2 degree differential. 2 days ago I changed it to 3 and now it isn't turning on as much. It didn't make a difference if I ran 500gph thru my chiller or 1000 gph thru it. it still ran for 2minutes or less and back on in 4-5 minutes which doesn't make sense to me. Rate of flow should play a part on how long it stays on.
ALL of my chillers are doing the same thing. All of them have controls facing the wall so the condensers flow straight out into the room without restriction. I have windows open usually and ceiling fans on, Cabinet fan on my 92 is on 24/7. This is lengthy enough and I didn't want to list the parameters of the other 2 as well and I'm sure none of you want to read more as this I know is beyond pushing it. I jsut wanted to paint a full picture for anyone experienced enough to tell me if there is something else I should be doing. I'm getting fans to blow across the top of the tanks. I only have a 54 corner that has an open top and that's only because it broke.
My 92 has the most heat generated from equipment. My other 2 tanks only have t5's. I know this is high but it is what it is. I know in the high temp days that my chillers will need to do 30 degree drops from 95+ degree days so I just have everything in my tank acclimated to higher temps and everything looks happy and is thriving. Setpoint is set for 79 degrees with a 3 degree differential. When I had it set for 2 degrees it just turned on and off about 15-20 times in an hour. That's 6-8 hours in a 24 hour period TIMES 3 chillers. So she is gonna kill me when the bill comes in.
My thought is that (3) 1/4 hp chillers = 9000 btu's. If I run my A/c I'll be running 36-42,000btu's. So eventhough it isn't cheap it should be much cheaper but I know that my window a/c's don't run for 2 minutes and off for 5. They usually run for 5-10 and are off for 30 minutes or more. on/off, on/off is no good for any compressor in any refrigeration equipment. the 3 degree differential (although way wrong) is kinda more acceptable as far as time on verses time off ratio that I'm seeing now.
You all deserve a bottle of the finest top shelf liquor of choice for reading all of this. I promise to give you all a lap dance personally. j/k
Thanks for your time and any help will be appreciated.
Equipped with:
CPR overflow box with aqualift pump and filter for aqualift pump (LOUD AS ALL HELL)
Glass tops (small black plastic triangle is off)
Current nova extreme 4 bulb t5 156w with 2 daylights, 1 actinic and 1 purple + integrated fan (sits 1/2" off of glass)
Oddysea 18" metal halide 150w 10k with remote ballast (ballast is about 3 feet away from setup) with (2) 18w t5 actinics and integrated fan 186W TOTAL (raised on 3-4" legs)
Natural Wave wavemaker (3 outlets for powerheads) strapped to back of stand
(3) hydor koralia power heads 3,4 and 5 i think
Ecosystems refugium with 18w pc light (in stand)
CPR in-sump protein skimmer (rio 600)
Current Gamma 25w UV sterilizer (in stand)
Blueline 55 (90 watts) external pump (in stand) that goes to a 2 valve manifold
First valve goes to the main return which is full open to an Eheim spraybar about 24-30" long
Second valve is throttled down slightly as water passes thru the uv and chiller and then returns into a smaller Eheim spraybar with an elbow on the end without a cap as not to restrict flow I guess because it is too short maybe 8" in total
Current Prime 1/4 hp chiller which is next to the tank with control panel and display facing wall so condenser side blows into my living room without any restriction
4" RadioShack Server fan (I think) that blows a pretty serious amount of air. Enough that in the colder months I have to turn it off when I work under my tank 'cause it is too cool of a breeze. This fan is cut and mounted into the stand blowing into the stand.
....................................................................................................
My house is naturally warmer than most. I'm in a single family raised ranch with an attic above so it is more like I live on the second floor. My chiller was turning on 6-8 weeks ago and has gotten progressively worse as far as how often it runs. Back when we had 70 degree days or less it would turn on for 1-2 minutes and off for 10 minutes. Now with the warmer weather we were having last week it would be on for 1-2 minutes and off for 5 and back on again all day long. A few weeks ago the ambient temp in my house was 74-76 degrees. Now it is more like 80-84.
I started running my actinics at 6pm to 11 pm (so I can enjoy my tank after work) and my daylights run from 11PM all night until 7am where the actinics stay on for another hour. I started doing this to cut down on overheating the tank and to stop from draining my wallet over an electric bill with my chiller. NOTE: I have 3 setups so 3 chillers can be crazy to pay for. We really don't use ac unless we cant take it because we have lots of live plants in the house. Electric is cheaper in the off-peak hours.
36" Current light cooling fan exhausts thru the back ( I guess for closed canopy applications) and the MH is behind it as my tank gets narrower towards the back because it is a corner tank. Point being that the cooling fan from the 36" light blows through the beam of light from the 150w MH so you can hold your hand under the MH and it only feels slightly warmer but not hot.
When my hand is in the tank and I raise it to just below the surface i can feel a pretty dramatic temperature difference from the rest of the tank to water surface. This is why I removed the black triangle so heat can escape but I don't think it helped much.
I bought this setup second hand.
The only problems that I noticed which I will/have correct/corrected are:
1) the chiller was in the stand and eventho the fan was added it is still a heat source. Now it is on the side of the tank. Putting it in the basement isn't really an option because that is my Landlord's storage space.
2) The blueline 55 has a 1" outlet that goes into a check valve and before it goes into the 2 valve manifold it is already reduced to 1/2" and both outlets off of the manifold are 5/8 tubing. I have to upsize the 1/2 into the manifold I think because it is a big restriction to go from 1" down to 1/2" without the pressure having a place to go. My thinking is that the water may be slowed down a bit too much and is absorbing heat from my blueline pump. I hear that they are heat machines but if the water is slowed down too much then I imaging that it would just amplify the issue.
My tank gets minimal sunlight which is mostly indirect. When it really starts to get hot I will pull down the shades.
The small black triangle on the back of the glass canopy is off to help heat escape and so that my MH can brighten up the dark spot of my tank.
Tank has about 150#'s of live rock and about 50#'s of dead skeletal corals that I've cured to use as live rock and a ph buffer
.......................................................................................................
Simple math got me thinking:
blueline 55 is rated for upto 1100gph and upto 28 ft of head. If I was getting 1100 (which I know I'm not) and If i had 100 gallons between refugium and DT. It would take 6 minutes for the tank to go thru my Chiller but my chiller runs for less than 2 minutes and turns back on in 5 minutes. These past 2 rainy days it hasn't come on much at all so I know it isn't just stuck in some kinda crazy cycle. But I changed it's program. Before when it was turning on and off all day long it had a 2 degree differential. 2 days ago I changed it to 3 and now it isn't turning on as much. It didn't make a difference if I ran 500gph thru my chiller or 1000 gph thru it. it still ran for 2minutes or less and back on in 4-5 minutes which doesn't make sense to me. Rate of flow should play a part on how long it stays on.
ALL of my chillers are doing the same thing. All of them have controls facing the wall so the condensers flow straight out into the room without restriction. I have windows open usually and ceiling fans on, Cabinet fan on my 92 is on 24/7. This is lengthy enough and I didn't want to list the parameters of the other 2 as well and I'm sure none of you want to read more as this I know is beyond pushing it. I jsut wanted to paint a full picture for anyone experienced enough to tell me if there is something else I should be doing. I'm getting fans to blow across the top of the tanks. I only have a 54 corner that has an open top and that's only because it broke.
My 92 has the most heat generated from equipment. My other 2 tanks only have t5's. I know this is high but it is what it is. I know in the high temp days that my chillers will need to do 30 degree drops from 95+ degree days so I just have everything in my tank acclimated to higher temps and everything looks happy and is thriving. Setpoint is set for 79 degrees with a 3 degree differential. When I had it set for 2 degrees it just turned on and off about 15-20 times in an hour. That's 6-8 hours in a 24 hour period TIMES 3 chillers. So she is gonna kill me when the bill comes in.
My thought is that (3) 1/4 hp chillers = 9000 btu's. If I run my A/c I'll be running 36-42,000btu's. So eventhough it isn't cheap it should be much cheaper but I know that my window a/c's don't run for 2 minutes and off for 5. They usually run for 5-10 and are off for 30 minutes or more. on/off, on/off is no good for any compressor in any refrigeration equipment. the 3 degree differential (although way wrong) is kinda more acceptable as far as time on verses time off ratio that I'm seeing now.
You all deserve a bottle of the finest top shelf liquor of choice for reading all of this. I promise to give you all a lap dance personally. j/k
Thanks for your time and any help will be appreciated.