The air conditioner in my boat is a 110 volt unit that is water cooled.
It takes F22 freon. I added freon and now it shuts off on high preasure. I keep removing freon but it still shuts off in a few minutes.
The water supply is good, no clogged filters.
I don't have guages any more but I borrowed some when I added freon.
Any Ideas or would you want to come over and take your girlfriend on a moonlight cruise? Bring your guages. :)
 

Paul B

Advanced Reefer
Vendor
Rating - 100%
28   0   0
I would have to bring guages back to the boat because I forgot the numbers, but the stats are printed on the unit. It seemed like after I added freon, sometimes the reading would jump very high. But I filled it to the amounts it stated.
It now runs about 2 minutes and cuts off, the digital guage reads Hi
 

emmanuel

Advanced Reefer
Location
astoria
Rating - 100%
158   0   0
I'm not a pro but am a DIYer and have come across the same problem in my case on a car it was a clogged dryer/filter they tend to go bad from what I was told over time from absorbing moisture
 

mmike1992

Advanced Reefer
Location
New jersey
Rating - 100%
45   0   0
1--check to make make sure there is water going thru the water jacket i am assuming that it is sea water
2----if you addded freon thru the service valves make sure they are back seated stem on valve all the way out (unless the port is being used for pressue control then all the way out and 1/4 turn in )
3---high head in that short of time should be easy to find reason
--- your head pressure should be no more than 225 pounds if you over charged

thasts a couple to get you started
 